What is Leakge L Timeout Alarm on a Parker AC Drive?

Started by rickpend, October 06, 2016, 02:32:PM

Previous topic - Next topic

rickpend

What is Leakge L Timeout Alarm on a Parker AC Drive?

What is Parker LEAKGE L TIMEOUT alarm mean on a Parker AC drive? I'm looking for a simple explanation as to what Leakage L Timeout means.

And how do you clear the "leakage l timeout" alarm from a Parker AC drive?
Have a good day,
+++ Rick +++

(Moore OK Industry Team Member)

tomtester

Quote from: rickpend on October 06, 2016, 02:32:PM
What is Leakge L Timeout Alarm on a Parker AC Drive?

Here's what the manual says: The leakage inductance measurement requires a test current to be inserted into the motor. It has not been possible to achieve the required level of current. Check that the motor is wired correctly.

It seems as though you would only see this message on a new installation, but it can also appear in the event of a motor wiring issue or an open motor winding. You will need to research your motor connections and continuity to clear this alarm.
Best regards,
Tom Tester