What does E03 Mean on Hitachi SJ200

Started by travis, May 28, 2017, 06:33:AM

Previous topic - Next topic

travis

What does E03 Mean on Hitachi SJ200?

Looking for some help with some Hitachi SJ200 Errors. I'm not sure if you call these errors, faults, or alarms but I can use some detailed info and troubleshooting suggestions.


  • Hitachi E03 Alarm
  • Hitachi E03 Error
  • Hitachi E03 Fault

Thanks in advance!

drives-technician

#1
E03 Error / E03 Fault / E03 Alarm

Means: Overcurrent during "acceleration"

Possible Causes: Inverter output was short-circuited, or the motor shaft is locked, or the load is too heavy, or a dual-voltage motor is wired incorrectly.

Note: The Hitachi SJ200 will over current trip at nominally 200% of rated current.

Also, Hitachi SJ200 inverters will trip on over-current to protect the inverter. The motor output turns OFF, hence the motor free-wheels to a stop. Just press the Stop/Reset key to reset the inverter and clear the error.