What is Mag Current Fail Alarm on a Parker AC Drive?

Started by rickpend, October 06, 2016, 01:13:PM

Previous topic - Next topic

rickpend

What is Mag Current Fail Alarm on a Parker AC Drive?

What is Parker MAG CURRENT FAIL alarm mean on a Parker AC drive? I'm looking for a simple explanation as to what Mag Current Fail means.

And how do you clear the mag current fail alarm from a Parker AC drive?
Have a good day,
+++ Rick +++

(Moore OK Industry Team Member)

tomtester

Quote from: rickpend on October 06, 2016, 01:13:PM
What is Mag Current Fail Alarm on a Parker AC Drive?

This is from the manual: It was not possible to find a suitable value of magnetizing current to achieve the required operating condition for the motor. Check the motor data is correct, especially nameplate rpm and motor volts.
Also check that the motor is correctly rated for the drive.

It seems like this alarm can only be cleared by verifying and adjusting your calibration. This alarm is triggered by motor settings in particular or possibly an incorrectly sized drive for the motor that you're trying to control.

Best regards,
Tom Tester