What is Motor Stalled Alarm on a Parker AC Drive?

Started by rickpend, October 06, 2016, 10:22:AM

Previous topic - Next topic

rickpend

What is Motor Stalled Alarm on a Parker AC Drive?

What is Parker MOTOR STALLED alarm mean on a Parker AC drive? I'm looking for a simple explanation as to what Motor Stalled means.

And how do you clear the motor stalled alarm from a Parker AC drive?
Have a good day,
+++ Rick +++

(Moore OK Industry Team Member)

tomtester

Quote from: rickpend on October 06, 2016, 10:22:AM
What is Motor Stalled Alarm on a Parker AC Drive?

The troubleshooting manual says: The motor has stalled (not rotating).

1. Motor loading too great
2. Current limit level is set too low
3. Stall trip duration is set too low
4. Fixed or auto boost levels are set too high

To clear the motor stalled alarm you'll need to research your calibration settings including the setting mentioned in the troubleshooting guide. Also check the physical loading to make sure it moves freely or appropriately.

Best regards,
Tom Tester