Title: What is 24V Failure Alarm on a Parker AC Drive?
Post by: rickpend on October 06, 2016, 11:06:AM
What is 24V Failure Alarm on a Parker AC Drive?

What is Parker 24V FAILURE alarm mean on a Parker AC drive? I'm looking for a simple explanation as to what 24V Failure means.

And how do you clear the 24v failure alarm from a Parker AC drive?
Title: Re: What is 24V Failure Alarm on a Parker AC Drive?
Post by: tomtester on October 11, 2016, 08:53:AM
Quote from: rickpend on October 06, 2016, 11:06:AM
What is 24V Failure Alarm on a Parker AC Drive?

From the Manual: The 24V customer output has fallen below 17V. 24V customer output is short circuited. (Excessive loading)

Most likely mis-wiring of the 24V output or a short circuit to the load or the relay connected at this point. This problem can easily be resolved by temporarily disconnecting the load and troubleshooting from there...